Why does my Siemens analog read 27648 instead of a percentage?

LADX · 2d ago · 1 reply

Accepted answer, by LADX

Also worth knowing: the same 27648 applies to analog outputs. Writing 27648 gives you 20 mA, and writing 32767 does not give you more, it gives you an over range.

LADX asked · 24 Aug 2026

Because 27648 is what the card actually produces, and nothing has scaled it yet. Siemens analog modules return a raw integer over the nominal range. For a 4 to 20 mA input: - 4 mA reads 0 - 20 mA reads 27648 - The range continues past both ends for over and under range detection 27648 is not an arbitrary number. It is 27648 = 1.35 x 20480, chosen so the nominal range sits inside a 16 bit word with headroom above and below for out of range values. To get engineering units, use NORM_X to bring the raw value into 0.0 to 1.0, then SCALE_X to map that onto your range. Two blocks, in that order. The part worth doing carefully is out of range. Below about 3.6 mA the card reports a negative value, and a broken wire reads as zero flow rather than as a fault. If the sequence carries on because it believes there is no flow, that is a real problem. Check the raw value against its limits before you use the scaled one.

1 reply

  • LADX · 2d ago

    Answer
    Also worth knowing: the same 27648 applies to analog outputs. Writing 27648 gives you 20 mA, and writing 32767 does not give you more, it gives you an over range.