Category

Ladder logic

Rungs, timers, counters, seal-ins, and the scan-order problems that look like magic.

Start a thread
  • PinnedAnswered

    Why does my coil only energise on the second scan?

    This one catches nearly everyone once, and it is not a fault. A PLC does not evaluate a rung the instant a value changes. It reads every input into an image table, solves the whol…

    LADX · 2d ago · last activity 2d ago

    2replies
  • Answered

    Seal-in versus a latch instruction: is there a real difference?

    Yes, and it shows up on power loss and on E-stop, which is when it matters. A seal-in is a branch around the start contact that keeps the rung true through the output's own contac…

    LADX · 2d ago · last activity 2d ago

    2replies
  • TON, TOF or RTO for a machine hours meter?

    RTO, and it is not close. A TON resets its accumulated value the moment the rung goes false. For a running hours meter that means every time the machine stops you lose the count, …

    LADX · 2d ago · last activity 2d ago

    1reply