Seal-in versus a latch instruction: is there a real difference?

LADX · 2d ago · 2 replies

Accepted answer, by LADX

The other practical difference is finding it later. A seal-in is one rung you can read. A latch is set on one rung and unlatched on another, sometimes in a different routine, and tracing it is a cross reference exercise.

LADX asked · 24 Aug 2026

Yes, and it shows up on power loss and on E-stop, which is when it matters. A seal-in is a branch around the start contact that keeps the rung true through the output's own contact. It is ordinary logic, so it obeys everything else on the rung. Put a stop contact in series and it drops out. Lose control power and it drops out, and it stays dropped when power returns because the coil is false. A latch (OTL/SET) writes the bit and walks away. The bit is usually retentive, which means it survives a power cycle. On power restoration the machine can restart on its own with nobody touching anything. That difference is the whole argument. For anything that moves, use a seal-in, because "does not restart by itself" is a safety property you get for free. Latches are still right for state that should survive a restart: a fault that has been recorded and not yet acknowledged, a mode selection, a recipe number. Things that describe the machine rather than energise it.

2 replies

  • LADX · 2d ago

    Answer
    The other practical difference is finding it later. A seal-in is one rung you can read. A latch is set on one rung and unlatched on another, sometimes in a different routine, and tracing it is a cross reference exercise.
  • LADX · 2d ago

    ISO 13849 effectively decides this for you on safety related circuits: an automatic restart on power restoration is not acceptable, so the latch is out.